Coating Solution for demineralized water storage tank
Dear Members,

Could your suggest an arc spray coating for the internal of a tank storing demineralized water ? The PH value is 7. What should be the coating thickness and your recommendation of sealant ? What life can be expected of the coating ?

Thanks & Regards,

Raghav
Reply
01-14-2008, 04:25 PM,
#2
RE: Coating Solution for demineralized water storage tank
Hi Raghav

I would consider zinc or aluminium ~ 0.25 mm thick. Unsealed this could give in excess of 20 years life.
Reply
01-15-2008, 03:35 PM,
#3
RE: Coating Solution for demineralized water storage tank
Gordon Wrote:Hi Raghav

I would consider zinc or aluminium ~ 0.25 mm thick. Unsealed this should give in excess of 20 years life.

Thanks for your reply, however on the below mentioned link it states that the corrosion rate of zinc coating in demineralized water is 137 microns per year. Is that correct ? Any hands on experience ?

(link dead)

Thanks Regards,

Raghav
Reply
01-15-2008, 06:56 PM,
#4
RE: Coating Solution for demineralized water storage tank
Hi Raghav

Interesting site you linked to Big Grin

First apologies for my rather rash statement
Quote:Unsealed this should give in excess of 20 years life.
and will edit it to say could instead of should Ashamed0002 Estimating/predicting life is difficult due to the number of variable factors like temperature, agitation, composition, dissolve gases, pH etc. along with the fact that in real life cases we have to wait so long for results.

That said I can't help feeling a corrosion rate of 0.137 mm/yr sounds excessive, which would predict 0.250 mm zinc coating lasting only 2 years Sad Without knowing the exact conditions of testing it is difficult to comment.

I know some of the information we use to predict corrosion rates is from galvanised steel, but generally corrosion rates are based on the amount of zinc and whether applied by hot dip, plating or thermal spray seems to make little difference. One advantage of thermal spray coatings is the ability to use thicker coatings.

Some intersting links which may generate more discussion than answers Happy0193
(links dead)
Reply
05-17-2009, 06:53 AM,
#5
RE: Coating Solution for demineralized water storage tank
(01-09-2008, 01:23 PM)Raghav Wrote: Dear Members,

Could your suggest an arc spray coating for the internal of a tank storing demineralized water ? The PH value is 7. What should be the coating thickness and your recommendation of sealant ? What life can be expected of the coating ?

Thanks & Regards,

Raghav


Do u have design calculation for demineralized water storage tank.
Reply
05-17-2009, 01:07 PM,
#6
RE: Coating Solution for demineralized water storage tank
I don't think that Thermal Spray has a solution for this scenario.

Polyurea (elastomeric) coatings are currently the only viable and long lasting solution. They faciliate the longest lasting ptotection of any Carbon steel tank lining against the leaching nature of Demineralised water and VOCs (Volatile Organic Contaminants).

The only other option is to make the tank out of Stainless Steel tank - way more expense!

cheers

GlenB
Reply
05-18-2009, 04:04 PM,
#7
RE: Coating Solution for demineralized water storage tank
Hi,

I've recently been working with the water regulation authority for the approval for coating potable water containers with Zinc for anticorrosion - and it turns out to be a bit of a minefield.

The approvals body are there to approve organic coatings and therefore won't approve a metal coating - although it's a catch 22 because a metal coating doesn't require an approval....... It's like taking your bicycle for an MOT test. However of course the local water authorities won't let you apply anything without WRAS approval...Aaarg! Even more annoying is that Zinga (basically a heavily zinc loaded paint) is approved!

There is a US standard for zinc lining potable water tanks.

However you just said de-mineralised, so I'm guessing not for drinking water anyway?

Based on previous testing (kure beach etc) and textbook application of a zinc coating I would have thought that 20years is perfectly achievable for a thermally sprayed zinc coating?
Simon Hiiemae
Sulzer Metco (UK) Ltd
01633 488 091
emailaddressisSimon.Hiiemae@Sulzer.com
Reply




Possibly Related Threads…
Thread Author Replies Views Last Post
  Request for solution to reduce porosity in HVOF Tungsten Carbide Coatings sreenuvundela 7 12,288 07-22-2020, 08:01 AM
Last Post: Simon Kim
  thermal spray coating for Galvalume tank horsecheng 10 12,809 06-05-2020, 03:00 PM
Last Post: plzc126330
  Hot Salt Bath Solution mmgerrie 10 5,374 07-29-2019, 06:11 PM
Last Post: Lemster68
Lightbulb Problem solved Grinding solution for Hastalloy HVOF coating plzc126330 3 4,266 05-28-2019, 01:08 PM
Last Post: velocity
  Coating solution needed for slurry pump application Killswitch 11 12,421 02-19-2015, 02:57 AM
Last Post: Axis Machine
  LPG tank mlavar 1 3,358 07-10-2013, 05:42 PM
Last Post: loriolo
  gypsum Tank shantanu 4 5,286 06-25-2013, 05:56 AM
Last Post: Vijay Deshpande
  Tank that cant be blasted, ideas? stuartred4d 9 8,000 06-25-2013, 05:51 AM
Last Post: Vijay Deshpande
  Coating options for large carbon steel tank Jimmy D. 9 12,963 12-15-2010, 07:50 AM
Last Post: ives
  place propane tank upside-down as liquid service tank? pulaunias 7 31,263 10-18-2010, 05:19 PM
Last Post: djewell
  Coating on Sodium Hypo Chloride - 6-14% active Chloride- tank iwan-sedaryawan 1 5,111 09-11-2008, 12:50 PM
Last Post: Gordon
Rolleyes Etching solution for T800 Phdstudent 2 7,337 04-15-2008, 04:31 PM
Last Post: Phdstudent



Users browsing this thread: 1 Guest(s)





Surface Engineering Forum Sponsor - Alphatek Hyperformance Coatings Ltd