RE: Liquid Propane vs Vapor Propane
Hi Stephen
to the Surface Engineering Forum.
Taking the density of propane gas to be 1.83 kg/cubic metre which I think is based on 25 C at atmospheric pressure.
This should give you 546 l/kg @ 25C
Measuring in NLPM, I believe is based on 0 C @ 1 atm.
Correcting using Charles Law V1/T1 = V2/T2 where V = volume (m3 ) T = absolute temperature (K)
We get around 500 l/kg (0 C, 1 atm or NL normal litres)
Hope that helps
|
|
12-28-2007, 04:54 AM,
|
|
Stephen Booth
SuperMember
|
Posts: 270
Threads: 23
Joined: Dec 2007
Reputation:
11
| |
RE: Liquid Propane vs Vapor Propane
Thanks Gordon, that number seems about right to me. From a USA Website, that is supplying Propane to households, they indicate the liquid to vapor conversion factor at 1:270 which sound reasonable.
On a similar subject, we found that the 45kg tanks of Propane were freezing the lines, regulators and indeed even the flowmeters when the tanks were in the 100% full condition. We were using 3 tanks. We swapped out one full tank (out of the three) with a 1/2 full tank, allowed the sistem to normalize, and the freezing went away. Maybe caused by the full tanks drawing off liquid propane as well as vapor into the lines, the vapor evaporate in the lines, cooling and freezing?? Sound about right.
Thank much for the help.
Gordon Wrote:Hi Stephen
to the Surface Engineering Forum.
Taking the density of propane gas to be 1.83 kg/cubic metre which I think is based on 25 C at atmospheric pressure.
This should give you 546 l/kg @ 25C
Measuring in NLPM, I believe is based on 0 C @ 1 atm.
Correcting using Charles Law V1/T1 = V2/T2 where V = volume (m3 ) T = absolute temperature (K)
We get around 500 l/kg (0 C, 1 atm or NL normal litres)
Hope that helps
|
|
12-29-2007, 04:52 PM,
|
|
Gordon
Administrator
|
Posts: 1,802
Threads: 70
Joined: Jun 2006
Reputation:
9
| |
RE: Liquid Propane vs Vapor Propane
Hi Stephen
Basically, you need to know the mass of gas in your cylinder and the density of the gas under conditions of use to estimate consumption. Obviously, gas density is dependent on conditions of temperature and pressure. Unfortunately, gas suppliers don't always state the conditions for their gas density or use different temperatures like 25, 20, 15 C or 70, 60 F. If you are using gas flow parameters in NLPM for calculations (which is not necessarily the same as your direct flow meter tube reading, look in process manual for flowmeter reading vs SLPM or NLPM) the gas density value needs to be under conditions of 0 C and 1 atm for your calculations. You only need to consider ambient conditions when first establishing the true flow in NLPM.
Lets take your gas density figure of 1.97 kg/m3, without conditions it is not very helpful. If we say for example conditions are 25C @ 1.0132 bar (1 atm) then we can roughly correct this for 0C @ 1.0132 bar (1 atm) conditions using V1/T1 = V2/T2 where V = volume (m3 ) T = absolute temperature (K)
1 kg of gas with density 1.97 kg/m3 @25C, 1atm will yield 0.508 m3
0C = 273.15K, 25C = 297.15K
V1/T1 = V2/T2 or V2 = V1.T2/T1
V2 = 0.508 x 273.15 / 298.15 = 0.465 m3 for 1 kg gas @ 0C, 1 atm
So corrected density will be 2.15 kg/m3
Changing from propane to a propane/butane mix you may need to consider the different calorific, oxygen requirement and flame temperature differences. This could impact on process and coating quality and may require parameter/coating optimisation.
Propane does suffer problems with drawing liquid or condensation in pipework/flow meters and poor flow stability due to changes in temperature. Warming cylinders/pipework or much better using vaporisers is the best solution to this problem.
http://www.tssea.co.uk/pdf_files/coating...r-2003.PDF
Hope that helps
|
|
12-30-2007, 04:43 AM,
|
|
Stephen Booth
SuperMember
|
Posts: 270
Threads: 23
Joined: Dec 2007
Reputation:
11
| |
RE: Liquid Propane vs Vapor Propane
Gordon,
Thank you very much for the reply, it is indeed helpful, and answers many questions that I have. The TSSEA Publication was also very helpful.
Thank you very much.
Stephen Booth
Teknokraft Asia
stephen.booth@teknokraft.com
Gordon Wrote:Hi Stephen
Basically, you need to know the mass of gas in your cylinder and the density of the gas under conditions of use to estimate consumption. Obviously, gas density is dependent on conditions of temperature and pressure. Unfortunately, gas suppliers don't always state the conditions for their gas density or use different temperatures like 25, 20, 15 C or 70, 60 F. If you are using gas flow parameters in NLPM for calculations (which is not necessarily the same as your direct flow meter tube reading, look in process manual for flowmeter reading vs SLPM or NLPM) the gas density value needs to be under conditions of 0 C and 1 atm for your calculations. You only need to consider ambient conditions when first establishing the true flow in NLPM.
Lets take your gas density figure of 1.97 kg/m3, without conditions it is not very helpful. If we say for example conditions are 25C @ 1.0132 bar (1 atm) then we can roughly correct this for 0C @ 1.0132 bar (1 atm) conditions using V1/T1 = V2/T2 where V = volume (m3 ) T = absolute temperature (K)
1 kg of gas with density 1.97 kg/m3 @25C, 1atm will yield 0.508 m3
0C = 273.15K, 25C = 297.15K
V1/T1 = V2/T2 or V2 = V1.T2/T1
V2 = 0.508 x 273.15 / 298.15 = 0.465 m3 for 1 kg gas @ 0C, 1 atm
So corrected density will be 2.15 kg/m3
Changing from propane to a propane/butane mix you may need to consider the different calorific, oxygen requirement and flame temperature differences. This could impact on process and coating quality and may require parameter/coating optimisation.
Propane does suffer problems with drawing liquid or condensation in pipework/flow meters and poor flow stability due to changes in temperature. Warming cylinders/pipework or much better using vaporisers is the best solution to this problem.
http://www.tssea.co.uk/pdf_files/coating...r-2003.PDF
Hope that helps
|
|
01-05-2008, 05:42 PM,
|
|
jeffsays163
Active Member
|
Posts: 35
Threads: 9
Joined: Dec 2007
Reputation:
2
| |
RE: Liquid Propane vs Vapor Propane
Hi, Steven, great to see you here! This is Jeff, you know who I am, as we meet almost each year. Same as you, I just joined this Forum in Dec. 2007, quite helpful and enjoyable here isn't it?
By the way, I am meeting the same problem when installing my new bought DJ2700, on its propane. Here is very cold so the propane is even liquidized in the flowmeter on the DJC panel. When each time I ignite it with Hydrogen, it light up, with beautiful diamond, then in about 3 - 4 second, it flameout, each time the same. It's really puzzling me, and I always think it has something to do with the propane. Do you have some advices? Maybe somewhere else I should try? Thank you!
See you in this Year!
Jeff.
Stephen Booth Wrote:Gordon,
Thank you very much for the reply, it is indeed helpful, and answers many questions that I have. The TSSEA Publication was also very helpful.
Thank you very much.
Stephen Booth
Teknokraft Asia
stephen.booth@teknokraft.com
Gordon Wrote:Hi Stephen
Basically, you need to know the mass of gas in your cylinder and the density of the gas under conditions of use to estimate consumption. Obviously, gas density is dependent on conditions of temperature and pressure. Unfortunately, gas suppliers don't always state the conditions for their gas density or use different temperatures like 25, 20, 15 C or 70, 60 F. If you are using gas flow parameters in NLPM for calculations (which is not necessarily the same as your direct flow meter tube reading, look in process manual for flowmeter reading vs SLPM or NLPM) the gas density value needs to be under conditions of 0 C and 1 atm for your calculations. You only need to consider ambient conditions when first establishing the true flow in NLPM.
Lets take your gas density figure of 1.97 kg/m3, without conditions it is not very helpful. If we say for example conditions are 25C @ 1.0132 bar (1 atm) then we can roughly correct this for 0C @ 1.0132 bar (1 atm) conditions using V1/T1 = V2/T2 where V = volume (m3 ) T = absolute temperature (K)
1 kg of gas with density 1.97 kg/m3 @25C, 1atm will yield 0.508 m3
0C = 273.15K, 25C = 297.15K
V1/T1 = V2/T2 or V2 = V1.T2/T1
V2 = 0.508 x 273.15 / 298.15 = 0.465 m3 for 1 kg gas @ 0C, 1 atm
So corrected density will be 2.15 kg/m3
Changing from propane to a propane/butane mix you may need to consider the different calorific, oxygen requirement and flame temperature differences. This could impact on process and coating quality and may require parameter/coating optimisation.
Propane does suffer problems with drawing liquid or condensation in pipework/flow meters and poor flow stability due to changes in temperature. Warming cylinders/pipework or much better using vaporisers is the best solution to this problem.
http://www.tssea.co.uk/pdf_files/coating...r-2003.PDF
Hope that helps
|
|
03-02-2008, 09:10 AM,
(This post was last modified: 03-02-2008, 09:11 AM by jeffsays163.)
|
|
jeffsays163
Active Member
|
Posts: 35
Threads: 9
Joined: Dec 2007
Reputation:
2
| |
RE: Liquid Propane vs Vapor Propane
Hi, ycwbycwb, thank you very much, its such a difficult name though. Now I have finally solved this problem! The causes combined the magnetic valves (those for controlling the ignition etc.), CPU frame and flame detector faults. Before working it out, the DJ2700 had been put away for one year. so its not hard to imagine so many problems it had. My experience is after purchasing a machine, we's better use it, otherwise it will turn bad and losing the warranty. By the way, im using heating belt. Does it make differences? Thank you!
|
|
03-02-2008, 09:58 AM,
|
|
ycwbycwb
Active Member
|
Posts: 39
Threads: 6
Joined: Dec 2007
Reputation:
2
| |
RE: Liquid Propane vs Vapor Propane
Hi, Jeff,
In cold days, the heating belt will help me to get enough and stable propane with only one tank.
With vaporizer I can use liquid propane with one hose put at the bottom of the tank.
BR,
ycwbycwb
jeffsays163 Wrote:Hi, ycwbycwb, thank you very much, its such a difficult name though. Now I have finally solved this problem! The causes combined the magnetic valves (those for controlling the ignition etc.), CPU frame and flame detector faults. Before working it out, the DJ2700 had been put away for one year. so its not hard to imagine so many problems it had. My experience is after purchasing a machine, we's better use it, otherwise it will turn bad and losing the warranty. By the way, im using heating belt. Does it make differences? Thank you!
|
|
04-09-2012, 12:42 PM,
|
|
RE: Liquid Propane vs Vapor Propane
Liquid propane and Vapor propane are two different things. Vapor propane is reasonable than liquid propane. As liquid propane is used in households.
_________________________________________
|
|
|