Does anybody know of a successful fuel flow rate setting to utilize that can help determine the capacities of an acetylene cylinder at cooler outside temperatures. I have gotten data that suggests 10% of the capacity of the cylinder per hour and also 17% of the capacity per hour. Real time data is all over the place at different outside atmospheric temperatures once it reaches 69 degrees but as soon as it gets 65 degrees f outside and I am flowing the required 55 scfh part parameters for a full 20 minutes. I cannot determine the tank capacity because the psi gauges a loss of 50 psi instead of the normal .7 to 1.5 at warmer outside (above 74 degrees f) temps. We have tank blankets that are installed on the tanks but the heating elements are not connected to a power source. I am required to monitor the psi gauge and stop when the readings reach a certain value and recertify the gas by spraying a new control sampling coupon on every set of tanks that the process utilizes. Is there a chart or graph available out there that shows the withdraw rates for a 390 cu ft cylinders at colder temperatures. What would be a good method to determine when the cylinders require changeout when they are cold.
Reply
12-04-2014, 12:18 AM, (This post was last modified: 12-04-2014, 12:20 AM by Met.Eng..)
#2
RE: acetylene flow limits for flame spray metco 6c
Hi,

We've some experiences with C2H2 high flow rates (80-100 liter/min). Work with high flow rates as specially occur some problems. First one is acetone problem. If you have to use high flow rates with acetylene you have to calculate max flow/acetylene bottle. If I remember correctly you have to get max 15 l/min per acetylene bottle. Other problem is you cant calculate acetylene how much more in the bottle with checking pressure. Couse acetylene bottles have porous sponge in their selfs and acetylene gas impregnated this porous sponge. So you can only calculate weigh if you want to know how much you used. Generally acetylene bottles get 9 kg c2h2 (if the bottle is new). On the other hand you dont use your bottle down the 1 bar. If you use the acetone comes in the bottle and the bottle service lifetime decrease.

Regards
Reply




Possibly Related Threads…
Thread Author Replies Views Last Post
  Staring procedure for 6p-II flame spray mgbaca1 0 146 01-23-2024, 08:11 PM
Last Post: mgbaca1
  Assembling a second-hand zinc flame spray setup? Gasket 6 1,167 01-22-2024, 12:09 PM
Last Post: MarkDattilo
  Flame spray parameters TurbineRepair 12 21,763 12-10-2022, 05:27 AM
Last Post: SakshiVerma
  Propeller shaft repair by flame spray in the cones area Iwan Sedaryawan CA 1 3,128 12-09-2016, 04:56 AM
Last Post: Stephen Booth
  Flame spray guns 5P, 5PII, Type N Hector Monjardin 1 3,808 11-17-2016, 10:35 PM
Last Post: mgbaca
  Build up with Powder Flame Spray Met.Eng. 8 10,593 05-30-2016, 12:08 PM
Last Post: Gordon
  Wire Flame spray and Twin Arc spraying wtaz 1 4,190 03-30-2015, 09:41 PM
Last Post: loriolo
  Technology of Flame Spray -old and new Boris Eizner 0 3,319 01-29-2015, 10:04 AM
Last Post: Boris Eizner
  acetylene cylinder heating blankets chromalloymachi112 2 4,335 12-20-2014, 08:21 AM
Last Post: loriolo
  Sense Powder flow k09 19 20,136 09-12-2013, 01:59 AM
Last Post: Esteban
  "Flame Spray Handbook" sal 0 4,801 04-28-2013, 07:49 PM
Last Post: sal
  Throwing power limits of CVD? sgd27 0 2,491 01-23-2013, 03:26 AM
Last Post: sgd27
  DJ2700 low fuel gas flow guang 1 4,165 12-23-2012, 04:30 PM
Last Post: Gordon
  16 E flame spray sal 4 6,524 09-17-2012, 08:32 AM
Last Post: loriolo
  powder flow not coaxial (HELP!) CHI3 6 6,935 09-13-2012, 02:37 PM
Last Post: loriolo



Users browsing this thread: 1 Guest(s)





Surface Engineering Forum Sponsor - Alphatek Hyperformance Coatings Ltd